Hello. I’m working on Gen 2 Front and rear doors. Linear operators. Belt was broke on rear doors. Replaced belt and realized doors were shutdown.plugged Service tool into door operator. Says SHD DED. the only input high is LOS .. there were faults in the log but I cleared them to quickly to make note of them. LEDs seem ok. Green blinking. Red steady. Yellow led came on after playing with buttons on top Anybody have info on these operators? Power coming in is good. 240v
Last edited by Jluff; 11/07/22 04:44 PM.
08/11/2022 1:38 am
After replacing the belts, did you learned the travel?
Topic starter
08/11/2022 2:00 am
No. I saw that it said SHD DED. And I stopped there. I need info on how to work on these doors . Do you have run learn procedures? Is that normal occurrence after losing belt? I have replaced these belts b4 with out any other issues . There is no power on the doors. Have to close by hand to move the car. This is a glide operator
Last edited by Jluff; 11/07/22 06:10 PM.
Topic starter
08/11/2022 2:41 am
I have a manual I found from Unitec. I will be back tomorrow.
Topic starter
08/11/2022 10:42 pm
All my board functions and power check out good. My status lights all are acting as they should . 240v to P1. No P3 connection. P4 pin 1 to 3 has proper voltage. 24v discrete input. My DCP voltage is correct. 24v when away from sensor. 0 v when on sensor. I can see values change on my service tool as I move door by hand. Service tool plugged into door board says SHD DED. I never get any voltage to my 3 wire motor connector. But I never get the board to say ready. As soon as I do a learn run from the buttons on top of door board it aborts the learn .
09/11/2022 11:04 am
Is it an at400
Topic starter
09/11/2022 5:59 pm
Glide
Topic starter
09/11/2022 10:57 pm
A learn travel solved this problem. After repeated attempts lol
10/11/2022 1:43 am
Awesome