18/04/2024 9:35 pm
Hi
I have a 2 stop ESCO elevator intermittent shutting down.
Wiring diagram # DC -89-10618
Does any one have a print and any common problems with this thing. All small relays most 110v and bunch of artisan time capsules . I always find it on the bottom floor. Door will open but calls don’t stay latched
Topic starter
18/04/2024 9:59 pm
Also forgot to mention a main line reset fixes it and it will run all day. Seems to shut down every other day.
19/04/2024 3:48 am
Could it be the low oil timer?
Topic starter
19/04/2024 4:21 am
That’s a good idea. Does anyone have any documents that show me which timers are what.
19/04/2024 6:06 am
I looked at an esco print I have on my phone and it looks like they use MT as the low oil timer
Topic starter
19/04/2024 5:54 pm
Nobody has a print they can share ??? No ESCO pros out there ? Lol
19/04/2024 7:08 pm
What year is the controller? I may have something close
Topic starter
19/04/2024 7:38 pm
Hi. Thank you
This is the wiring diagram number
# DC -89-10618
480v
I think late 1980s but not sure
This is my email
[email protected]
Last edited by Jluff; 04/19/24 11:40 AM.
19/04/2024 10:33 pm
I sent you a pm
26/04/2024 3:06 am
Did you figure this one out?
Topic starter
26/04/2024 3:16 am
Yes. It was the MLT timer There was 2 motor leads tied together where the connection was coming apart