E-5000 help

4 Posts
2 Users
0 Reactions
3,922 Views
 Romo
(@romo)
Active Member
Joined: 17 years ago
Posts: 3
Topic starter   [#12550]
I have a kone E-5000 that will run for a day or so and then shut down - Not a hard fault so it just keys back up. The fault is Safety String Fault. The Tool says to check continuity between Annuciator boards and check pins and connections and I have done this and all is good. Just reaching out to see if anyone else has had this issue. Also says to check a few relays on cpu and have done this also.I went as far as changing both Annuciator Boards to no avail.



   
Quote
(@john-jay)
Prominent Member
Joined: 17 years ago
Posts: 798

   
ReplyQuote
 Romo
(@romo)
Active Member
Joined: 17 years ago
Posts: 3

   
ReplyQuote
(@john-jay)
Prominent Member
Joined: 17 years ago
Posts: 798
 
The only thing I can recall about a 66 had to do with a brake problem. But since I worked on 3000's and 5000's I don't know which one that pertains to. You may want to check your brake voltage just to be sure. I think it was around 160vdc. also the normal brake ohmic value was in the 350 ohm range.One other thing I remember is I had a handrail chain rub a low voltage safety string wire intermittently, taking it to ground causing this type of error. Just a couple of thoughts.



   