Elevator Forum

Dover T4 brake issu...
 
Notifications
Clear all

Dover T4 brake issue

4 Posts
3 Users
0 Reactions
2,465 Views
(@upndwn72)
New Member
Joined: 17 years ago
Posts: 1
Topic starter   [#39556]
I have a T4 that will try to run and will shutdown on a 154 fault. Any help would be appreciated Thanks



   
Quote
(@elmcannic)
Honorable Member
Joined: 17 years ago
Posts: 635
 
72,
Not everyone here knows what a 154 fault is other than its brake related and it shuts down the unit.
So with not much info to go on, here are my thoughts;

1) Drive initiates and the brake picks too late causing rollback. Parameter check.
2) Drive initiates and brake switch doesn’t send correct signal that it’s indeed lifted. Check switch contacts.
3) Brake drags and comparator signals are beyond parameter tolerance. Clean and adjust brake components.
4) Sluggish brake pick similar to #3
5) Brake coil open. No brake picks at all. Check coil resistance.
6) Broken signal or bad contacts on brake relay. Check.
7) Low voltage on brake pick or hold if that’s part of the circuit. Check.
8) Faulty/loose brake switch hardware. Inspect.

Hopefully one of these common situations gets you out of the weeds and in the right direction.



   
ReplyQuote
(@gohana256)
Eminent Member
Joined: 17 years ago
Posts: 29
 
154 Brake Input Error - Indicates the brake input is not active when the brake is being commanded to lift. This
could occur because the brake regulator card has detected a fault condition and dropped the feed to BK1.
..Brake Regulator Card Fault Detected
.. Defective BK1 input



   
ReplyQuote
(@elmcannic)
Honorable Member
Joined: 17 years ago
Posts: 635

   
ReplyQuote
Share:
Scroll to Top