Elevator Forum

Dover relay logic o...
 
Notifications
Clear all

Dover relay logic oildraulic

19 Posts
1 Users
0 Reactions
26.3 K Views
(@Broke_Sheave)
Joined: 1 second ago
Posts: 0
 
Originally Posted By: GreenPants
on fridays never pull your tools out of the truck after lunch unless absolutely necessary.

You are indeed a wise man Green Pants.



   
ReplyQuote
 TKE
(@TKE)
Joined: 1 second ago
Posts: 0
 
UC,CC and DC are 32 volt relays (black coils) make sure know one has changed one out with a 48 volt or worse a yellow jacket.



   
ReplyQuote
 jkh
(@jkh)
Joined: 1 second ago
Posts: 0
Topic starter  
Green pant
There is wisdom in your words...

TKE
This unit uses 26 volt black coils for UC, DC, & CC. The prints at this job were in mint condition. The voltage difference is clearly indicated on the print. and Jim Collett reached out with a description of the canceling sequence for this circuit. So Monday when I walked into machine room I was good to go!

Thanks for the heads up.



   
ReplyQuote
(@Oleeightball)
Joined: 1 second ago
Posts: 0
 
I'm no fan of yellow jackets, or any other relative of bees personally.
Watch out for the wire slipping down in wcr relay those are FUN.....
Also the little plastic pieces that go around coils do get brittle and will cause you grief as well,
Here is a hint as well, put a change date on those with magic maker
After year or so I change them out.... Less trouble
And lest I forget the brass sleeve on 14/15 switches on composites....
For the new guys



   
ReplyQuote
Page 2 / 2
Share:
Scroll to Top