Dover DMC 1 getting Front door Internal Error

2 Posts
2 Users
0 Reactions
2,154 Views
(@weupnow)
Eminent Member
Joined: 17 years ago
Posts: 21
Topic starter   [#23756]
Working on a Dover DMC 1 was getting a fault saying defective control board not sending 150 volts to door operator, changed CLC board and now getting a fault saying Door Operator internal error, anybody have any suggestions



   
Quote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
If you have a PY2 or PY4 door board, make sure there is a Capacitor wired from P150 to G150 in the controller. Other than that and checking your 12v (10.75), I think all you can do is replace the door board.



   
ReplyQuote