Dover Composite leveling issues

5 Posts
3 Users
0 Reactions
7,136 Views
(@united-tech)
Trusted Member
Joined: 17 years ago
Posts: 35
Topic starter   [#14285]
Hey guys. I am trying to help out a co worker on this issue. Does not have optical leveling. We have two different elevators in two different cities. Ones a low rise the other is a 700fpm car. The problem is when the cars go to level into a floor they go into leveling speed nicely And slow down to the point were they almost stop, then speeds back up to leveling speed and hits the floor level. They do this on every single floor. Any ideas would be greatly appreciated. Compounding? Floor bar contacts?



   
Quote
(@united-tech)
Trusted Member
Joined: 17 years ago
Posts: 35
Topic starter  
Correction. The car almost slows down to a stop and then picks back up and levels to a floor. Only in down direction. Floor levels are good , speeds are good, brushes are good



   
ReplyQuote
 jkh
(@jkh)
Prominent Member
Joined: 17 years ago
Posts: 904
 
Look at the relay sequence pattern during deceleration. Like you said, two different cars. Which means the faster FPM car will have more steps.

Are any of the optical leveling LEDs on?

Last edited by jkh; 05/28/15 02:05 AM.


   
ReplyQuote
(@united-tech)
Trusted Member
Joined: 17 years ago
Posts: 35
Topic starter  
The sequencing is fine on the slower car but it turns out someone has jumped out one of the slowdown steps.



   
ReplyQuote
(@e-man)
Honorable Member
Joined: 17 years ago
Posts: 480

   
ReplyQuote