I had a 400a shut down with a bunch of these faults. Clear faults and it took off running was wondering if anyone could please tell me what this fault is so I can look into the problem.
Thanks
19/05/2017 10:01 pm
Will look and see but I bet some Schindler guys have the answer in their head.
Last edited by Rolly; 05/19/17 02:02 PM.
20/05/2017 7:07 am
Check door locks, might be clipping locks while running
22/05/2017 4:53 am
Hatch lock. ECI locks are some of the most unreliable locks in the industry.
24/05/2017 2:08 am
The safety circuit is open before the fourth tap (ISKT4) and after the third tap (ISKT3). "Extra Info" from the SMLCD screen can narrow it down