Circa 71, hoist motor had let the smoke out of it. Got a rebuilt one from the good folks in Florida. It runs very fast now, and it is tripping the 3p and or burning the 5/6 contact in the NL relay. Both of these are right in line with the Motor Armature.

Any ideas?



   
Quote
(@Fehlerteufel)
Joined: 1 second ago
Posts: 0
 
Hi,

sry have no idea what this is for a motor, but an idea I have anyway:
star-delta connection motor swapped



   
ReplyQuote
(@EElevator)
Joined: 1 second ago
Posts: 0
 
Sounds like your motor shunt fields might be too weak. That would explain the higher speed and armature current. If your shunt fields weakened it doesn't induce as much counter voltage into the armature windings, allowing more current to flow through the armature which makes more torque which equals it speeding up as well.



   
ReplyQuote
(@solidstate)
Joined: 1 second ago
Posts: 0
Topic starter  
Yes, some one suggested that the motor field voltage may be too weak.



   
ReplyQuote
(@solidstate)
Joined: 1 second ago
Posts: 0
Topic starter  
Do not think it is motor field voltage. We are over speeding in the inspection mode, and getting full voltage to the field on inspect.



   
ReplyQuote
(@EElevator)
Joined: 1 second ago
Posts: 0
 
Is this motor compound wound? If it is, are the series and shunt fields hooked up cumulative or differential?

Whats the armature voltage compared to nameplate full speed armature voltage? Is the motor simply getting more voltage than you want it to for inspection speed? Maybe the wrong generator field relays pulling in, or somehow some resistors in the controller are shorted?



   
ReplyQuote
(@solidstate)
Joined: 1 second ago
Posts: 0
Topic starter  
I will try to post what we find, got another tech coming in.



   