Elevator Forum

Requirement to prov...
 
Notifications
Clear all

Requirement to provide emergency power to elevator

2 Posts
1 Users
0 Reactions
2,207 Views
(@Tapan Katwala)
Joined: 1 second ago
Posts: 0
Topic starter   [#25687]
Hello,

I'd appreciate insights on the requirement to provide emergency / standby power to elevators during a power outage.

I understand that as per most building codes, for a building classified as a "high" building such as building 6 storeys and over, there is a requirement to provide at least one or all elevators on emergency / standby power. Would this be true or at least one (1) elevator is required to be on emegency / standby power?

What would be the requirment to provide emergency / standby power for elevator in buildings not classifed as "high" buildings i.e. buildings less than 6 storeys?

Thank you.



   
Quote
(@john jay)
Joined: 1 second ago
Posts: 0
 
The A17.1 elevator code states elevators provided with Standby power shall comply with 2.27.2.1 thru 2.27.2.5 it leaves the requirements up to the various building codes.



   
ReplyQuote
Share:
Scroll to Top