Topic starter
25/01/2014 11:09 pm
i need a print for a heller traction...mod#54.a...type20.3...s/n1073 it has an acceleration relay w/an"at"solid state timer &resistive grid please help
25/01/2014 11:44 pm
Is it a m/g job?
Topic starter
25/01/2014 11:59 pm
no...3phase w/L2 reading as ground @disconnect...checked supply from outside...only 2 lines +ground coming in...i have never seen 3 phase motors wired like this...my problem is potential wont pull in when a call is placed..safety relay is energized....finals &floor limits ok..i have voltage @ call stations
26/01/2014 5:47 am
A 2 speed AC?
26/01/2014 5:35 pm
how old is it???
Topic starter
27/01/2014 3:50 am
Yes...3phase
Topic starter
27/01/2014 4:02 am
It was installed 7/29/54
28/01/2014 12:59 am
Unfortunately the only heller prints I have are for a m/g job, a single spped AC and a hydro. Being Westinghouse bought Heller back in the day, maybe you could try Schindler Milwaukee. Where abouts is this job located?
Topic starter
28/01/2014 7:06 am
its in green bay....ill try milwaukee..thanks
12/03/2014 9:51 pm
Your L2 going to ground is called grounded "B" phase, very common in Milwaukee. East side.