TKE Endura MRL Dispatching

6 Posts
1 Users
0 Reactions
3,715 Views
(@Knoxville18)
Joined: 1 second ago
Posts: 0
Topic starter   [#32675]
We have a duplex that wont group together. We can make either car the master and it will take calls but it never sends calls to the slave car. We have checked all parameters and even compared them with another duplex group that we maintain. We didn't find anything out of the ordinary. Any suggestions on where to go next? We have even reloaded software. We're at a loss and are out of ideas. We don't get much help not being from TKE.



   
Quote
(@wltr00)
Joined: 1 second ago
Posts: 0
 
Check W11



   
ReplyQuote
(@Knoxville18)
Joined: 1 second ago
Posts: 0
Topic starter  
I read W11 as Swing car side parameter. I may not have the right book though. Are you thinking a car is on swing operation?



   
ReplyQuote
(@wltr00)
Joined: 1 second ago
Posts: 0
 
Yeah try W11 to either 1 or 3…can’t remember which but worked for me!



   
ReplyQuote
(@Knoxville18)
Joined: 1 second ago
Posts: 0
Topic starter  
We'll try it. Thanks



   
ReplyQuote
(@Knoxville18)
Joined: 1 second ago
Posts: 0
Topic starter  
We changed it to 0 and it worked. Thank you for your help.



   
ReplyQuote