Elevator Forum

Tiii safety string ...
 
Notifications
Clear all

Tiii safety string and generator

2 Posts
2 Users
0 Reactions
3,186 Views
(@elevatorpat)
Eminent Member
Joined: 17 years ago
Posts: 28
Topic starter   [#14460]
Hopefully someone can help:

Got a t3 shut down floor level at the top terminal. All the prints are very dated and incomplete. On the group computer my service status is "safeties" meaning the safety string is open.

I am losing safety circuit between prp (phase reversal protection I imagine) and the governor switch. The prp is fed from some other page of the prints that I don't have. I have tried jumping prp to no evail.

Anyone have any info or prints regarding the prp or how to get the generator to kick on? My prints are very limited, I assume in order for Gen to fire you must have a complete safety circuit?

My only relays that are high are dz, dz1 and another one (can't remember off the top of my head)

Gonna try replacing the field regulator board tomorrow...

Thank!



   
Quote
(@vatorgator)
Honorable Member
Joined: 17 years ago
Posts: 432
 
On a generic print i have, prp is fed from terminal LCS which is hot side of the line, through FP contact, then through the ACO and DCO which are ac overload, and dc overload contacts, then through a AUX1 and AUX2 contacts which note says will be open if circuit breaker is tripped. then to prp terminal. the Prp terminal then goes to the GEN output circuit which if cpu is turning on, will pick up GEN relay, then from prp terminal we come through a normally open GEN relay contact that then goes to the y+d starter coils. need to check to see if you have voltage from LCS to LCO. If you are good there, then you are open on one of the below terminal points, FP terminal for fp contact, OVL terminal for overloads, and CBK terminal for circuit breaker aux contacts

when you say you try jumping prp, where are you jumping from? LCO is the common, so you should have 120 vac at the above terminal points, if not that circuit is open. if you have voltage at prp, then you are open farther down the safety circuit. i have some generic prints, pm me your email and i will send them to you

Last edited by Vatorgator; 06/18/15 04:46 AM.


   
ReplyQuote