Elevator Forum

Tac 20 hoistway sca...
 
Notifications
Clear all

Tac 20 hoistway scan not completing in ims

4 Posts
1 Users
0 Reactions
3,676 Views
(@Getemup)
Joined: 1 second ago
Posts: 0
Topic starter   [#21098]
Working on a tac 20 and it is not completing hoistway scan in Ims, any suggestions as to why that may be? But unit is still running. Thanks



   
Quote
(@Indirtwetrust)
Joined: 1 second ago
Posts: 0
 
How far does it get? When the scan window is open, it should say Pass, Pass, then Fail at some point. What point? UNL is the last thing it needs to see.



   
ReplyQuote
(@elmcannic)
Joined: 1 second ago
Posts: 0
 
If you're trying to do a scan, there must be a reason. Or, are you just trying to learn a bit more about this control?

On the scan, at what point does it fail? The scan window should tell you.
If your having an intermittent fault, run the recorder also in IMS while running the car, and just maybe you'll catch it while you're there. Check the slowdown magnets for any gaps and correct.
Also, post the faults if you're lacking documentation.
DZ and DZE (and magnets gaps) are common selector faults that can be annoying and intermittent.



   
ReplyQuote
(@Getemup)
Joined: 1 second ago
Posts: 0
Topic starter  
Get three of them to pass just says incomplete, will post any faults. thanks



   
ReplyQuote
Share:
Scroll to Top