We are experiencing intermittent shutdowns on an elevator with Swift 5000 Controls. We have no monitor in place to help assess faults, but do have a laptop with only gives us fault codes, which we can then interpret from the documents in the machine room. Here are a list of faults we are getting and a brief description of what we have done. After completing all the below we continue to get intermittent faults.
Fault 11: Limit Position Reference Error: Replaced the power supply, new terminal limit at basement level
Fault 43: Gate and Lock Limit: Installed new gate contacts
Fault 31: Car in next up mode:
Fault 18: Car Response Time Out: Replaced Module, Replaced BK Relay, replaced MC Relay, replaced BK Module
Fault 27: BK and MC relay; replaced both relays
After all of the above we are still experiencing intermittent shutdowns. Floors served B, 1-15.
A modernization of this elevator (as well as all others) is currently in the works, however, at a minimum of 6 months out
Can anyone help with the above issues?
Secondly, does anyone know if there is a auto call mode on this type of control system where we can block the doors from opening, and run the car without the doors opening?
Your help is greatly appreciated
As far as running and not allowing the doors to open, all the swift cars I worked on had a toggle switch for that purpose.