Smartrise Question

2 Posts
1 Users
0 Reactions
1,488 Views
(@wltr00)
Joined: 1 second ago
Posts: 0
Topic starter   [#35609]
Anyone know the purposes of the fuses on the CXN board?
Thanks



   
Quote
(@Alex_ELMAN)
Joined: 1 second ago
Posts: 0
 
There are two 5A fuses.
One provides voltage to the Valves. If a valve shorts to ground or draws too much current for any other reason, it will blow the fuse. The other one apparently is connected to the Neutral side of the valves.



   
ReplyQuote