schindler 330A issue

3 Posts
1 Users
0 Reactions
5,438 Views
 mbke
(@mbke)
Joined: 1 second ago
Posts: 0
Topic starter   [#11164]
Hey bros of iuec. I have a 330A that will always get a 20 error with extra info 67.(possible PCT issue)always happens at the 3rd floor. I have changed the landing system , CRIP, and CIO board. CAP drain. Also made sure my UL Spring wasn't broken. Any body have anything on this?



   
Quote
 jkh
(@jkh)
Joined: 1 second ago
Posts: 0
 
You may want to check your leveling. I usually set it for 5 to 6 seconds! If the time is too great it can trip those errors.

Last edited by jkh; 07/02/14 12:37 AM.


   
ReplyQuote
(@mrhappy)
Joined: 1 second ago
Posts: 0
 
is 3rd floor the top landing? if so,schindler may want to park the car above the floor by an inch on a relevel to reduce the number of times it relevels. otis does this and it means the up normal is set to low. the 20 fault with a 67 is relevel stall for more than 7 seconds. try cracking manual lowering while parked at that floor and see if it faults.



   
ReplyQuote