Schindler 330A Fault

6 Posts
5 Users
0 Reactions
10.5 K Views
(@verticaltechny)
Estimable Member
Joined: 17 years ago
Posts: 75
Topic starter   [#16569]
Keep getting an intermittent 97 ETSL fault. It will go days without doing it and 9 times out of 10 the building guy has recycled the power and it's running on arrival. We have ruled out the sensors, all terminal connections, traveling cable wire



   
Quote
(@e-man)
Honorable Member
Joined: 17 years ago
Posts: 480

   
ReplyQuote
(@cucuvator)
Estimable Member
Joined: 17 years ago
Posts: 81

   
ReplyQuote
(@whadafack)
Trusted Member
Joined: 17 years ago
Posts: 80

   
ReplyQuote
 Ken1
(@ken1)
Eminent Member
Joined: 17 years ago
Posts: 19
 
Magnet or optical sensors? If its magnets try changing the reed switch, optical you need to change the black ets switch, usually only one goes bad but difficult to tellwhich when intermittent.



   
ReplyQuote
(@verticaltechny)
Estimable Member
Joined: 17 years ago
Posts: 75

   
ReplyQuote