Schindler 330A

4 Posts
1 Users
0 Reactions
9,091 Views
(@local yocal)
Joined: 1 second ago
Posts: 0
Topic starter   [#3873]
I have a stuck input on KHU. I replaced the board in the c.o.p and the main relay board in the controller. The only board left is the software board. Magnetic switches on cartop are ok and have been taken out of the equation. Any suggestions?



   
Quote
(@E-man)
Joined: 1 second ago
Posts: 0
 
Try shorting the cap on the GCIO360PCB - power off, pull GCIO360, short that big round cap (2 pins on back of PCB) for about 1 minute.

Last edited by E-man; 06/13/12 09:31 PM.


   
ReplyQuote
(@GreenPants)
Joined: 1 second ago
Posts: 0
 
best thing for a 330a and trx5 is the double reboot ram flush. on inspection push the reset button and as soon as the red light turns on again push and hold the reset for 5 sec. this clears the ram that is probably held charged by that cap.



   
ReplyQuote
(@local yocal)
Joined: 1 second ago
Posts: 0
Topic starter  
Software board fixed it



   
ReplyQuote