Elevator Forum

Schindler 3300 batt...
 
Notifications
Clear all

Schindler 3300 battery issue

6 Posts
1 Users
0 Reactions
10 K Views
(@Sammy)
Joined: 1 second ago
Posts: 0
Topic starter   [#22470]
3300 MRL keeps giving battery warnings and won't run on Automatic. Batteries are fine. I believe it's the SEMNA card as this has the charger on it that isn't doing it's job anymore. I'm leaning towards card replacement. Anyone experienced this issue yet?



   
Quote
(@koneisland)
Joined: 1 second ago
Posts: 0
 
Presume you're aware that you have to press yellow button to activate battery charging. If so change card.



   
ReplyQuote
(@FrenchTec)
Joined: 1 second ago
Posts: 0
 
Hi
Are you on the last version of 3300 (Bionic7) ?

If yes there's an issue with the SEM SW, if your version of sw SEM is under 2.8 (in CF12 PA4 you must see 280)
In that case update or replace the SEM and also the battery.

If older version of 3300 (rel2, rel4), if the voltage of your battery is low, the SEM can't charge.
The SEM is just able to keep the charge on top.



   
ReplyQuote
(@Scrapwood99)
Joined: 1 second ago
Posts: 0
 
Just curious where is this yellow button,?



   
ReplyQuote
 JJR
(@JJR)
Joined: 1 second ago
Posts: 0
 
If you have the North American version. This doc may help: https://firstchroniclesproductions.... trol%20System%20Basics%20REV%200.3.5.pdf



   
ReplyQuote
(@EElevator)
Joined: 1 second ago
Posts: 0
 
Just throwing this out there... batteries need to be load tested to determine if they are "fine" or not. If your just checking with your meter, that's a inaccurate test



   
ReplyQuote
Share: