Elevator Forum

Otis E411MMS contro...
 
Notifications
Clear all

Otis E411MMS controller fault 2854

7 Posts
1 Users
0 Reactions
8,438 Views
(@Jluff)
Joined: 1 second ago
Posts: 0
Topic starter   [#19181]
Working on an Otis E411 Last night had major power problems in the building .. I'm getting shutdown code 2854. SPT conn loss. Anybody have an advice ?



   
Quote
(@Rolly)
Joined: 1 second ago
Posts: 0
 
24V/Door Zone Sensors Lost..



   
ReplyQuote
(@Jluff)
Joined: 1 second ago
Posts: 0
Topic starter  
Are those the position transducers ?



   
ReplyQuote
(@Vatorgator)
Joined: 1 second ago
Posts: 0
 
SPT secondary postion transducer. loss of SOK input to mlb3 board. MLB3 board supplies 24 volts to cartop SPT unit. the wiring of the unit then sends the 24 volts back to the mlb3 board to verify 24 volts available at cartop unit. fairly simple to diagnose problem. look at print, possible blown fuse, bad mlb3 board, traveling cable etc. for some reason SOK input is not correct.



   
ReplyQuote
(@Jluff)
Joined: 1 second ago
Posts: 0
Topic starter  
Working with No print.



   
ReplyQuote
(@Jluff)
Joined: 1 second ago
Posts: 0
Topic starter  
it was a bad board. Txs guys.



   
ReplyQuote
 NUN
(@NUN)
Joined: 1 second ago
Posts: 0
 
Hi...
Friend, wich board was the failure?



   
ReplyQuote