30/05/2017 10:13 pm
LRV 5L
Had power problems in building
Doors r dead
No power to HES coils
No power to 20CI 1 thru 6
All Saftey circuits good
All fuses n power r good.
110v to 11CI 10 but don't power to 20CI 6
Think board is bad.
F2 fuse did not blow which is weird to me
What do u guys think ?
31/05/2017 5:42 am
Looks like door power comes right off taps of the transformer (PSD1-PSD2) and gets fused and rectified and sent straight to the operator. Did you diode check the rectifier and confirm your voltage to it?
Topic starter
31/05/2017 7:59 am
No. But I will. I think I ruled out the rectifier but don't remember why.
Txs JH
Txs JH
31/05/2017 9:51 am
When you say doors are dead, do DO and DC pick but doors don't move? You are only going to read voltage on 20CI-6 if DO and AUD are both picked. And are you saying NDG is picked but you have no voltage to HES? Does the car run on inspection?
31/05/2017 10:00 am
If none of the ice cube relays are picking, make sure you have 24vdc at DC6 through the F6 fuse. That 24v regulator on the board is a weak point. If it fails it can just be removed.
02/06/2017 5:12 am
Car station capacitor needs to be discharged, it locks elevator up.
Topic starter
02/06/2017 8:37 am
Txs Chicago. That was it.