KCM831 0072 Fault

3 Posts
1 Users
0 Reactions
1,454 Views
(@Updownman)
Joined: 1 second ago
Posts: 0
Topic starter   [#37514]
I'm Having intermittent 0072 fault on a KCM831 two stop. I have swapped sensors, checked magnet and sensor setups multiple times with shaft setups. It will run for about a week then it will come back in. I'm looking into replacing the LCECCBN2 next. If there is any other ideas please let me know.

Thanks!



   
Quote
 MX4
(@MX4)
Joined: 1 second ago
Posts: 0
 
If you have checked magnets, magnet distance, shaft setup, switch gap, switch then yes CCBN board could be failing

Last edited by MX4; 05/30/24 05:33 PM.


   
ReplyQuote
(@project.elevator)
Joined: 1 second ago
Posts: 0
 
Also, might be the travel cable issue, you can swap the wire that carry it signal for check.



   
ReplyQuote