Hi, with Dover computamatic controllers, I have problem with 4 elevators/15 story building. the dispatcher unit looks like disabled.
All elevators are running in wild operation (The elevators are running continuously between the floors and never stops , and the hall calls still stuck on and never cancel the calls.
We checked all the wiring between the dispatcher unit and the controllers; and even if we turn the dispatcher off the wild operations is still.
I could NOT figure out what is the problem and how we can re communicate these elevators with the dispatcher.
Thanks for helping,,,



   
Quote
(@Johnny)
Joined: 1 second ago
Posts: 0
 
What city are you in?



   
ReplyQuote
(@Johnny)
Joined: 1 second ago
Posts: 0
 
Check relay ATO, is it in? are all your wire contacts in ATO in good shape?



   
ReplyQuote
(@Johnny)
Joined: 1 second ago
Posts: 0
 
voltage from ATC to S+ ???



   
ReplyQuote
(@Johnny)
Joined: 1 second ago
Posts: 0
 
condition of NP Relay



   
ReplyQuote
(@EMEEL LLC)
Joined: 1 second ago
Posts: 0
Topic starter  
thank you very much.
i got the problem solved.
some wire in dispatcher came off by loose connector.
Thank you very much



   