DMC-1 Hoistway Scan Selector Fault

20 Posts
7 Users
0 Reactions
29.7 K Views
(@sbrmilitia)
Honorable Member
Joined: 17 years ago
Posts: 448
 
62 deals with the 2nd landing parity magnet. They prolly adjusted the leveling magnet and didn't move the 3inch. They need to get themselves a gauge and some info where the 2nd landing 3inch magnet goes.

Last edited by sbrmilitia; 03/18/14 10:45 PM.


   
ReplyQuote
(@halfpick)
Reputable Member
Joined: 17 years ago
Posts: 239
Topic starter  
Replaced the main and Aux reader board... no more 62 errors..Still not loading count..Selector board stays on with no heart beat? No selector fault now...CLC 35 Faults? I'm thinking CLC bad also...Reading parity bits and others variables when car is in middle of hatch? No magnet even close to it? Selector Board is a different board from water damage car so guessing it maybe OK?



   
ReplyQuote
(@halfpick)
Reputable Member
Joined: 17 years ago
Posts: 239

   
ReplyQuote
(@vatorgator)
Honorable Member
Joined: 17 years ago
Posts: 432
 
with all that water damage, clc probably bad. you can check the selector inputs by unplugging the communication cable from the selector that goes to the clc board. then plug into the db25 plug on the selector and check all the inputs, if you are still reading inputs when selector is not near any magnets, then you have problems with the selector assembly still. sounds like E-Mans advice maybe the best yet, replace all boards , and bill the customer. save yourself headaches down the road.



   
ReplyQuote
(@halfpick)
Reputable Member
Joined: 17 years ago
Posts: 239
Topic starter  
I would agree with you guy's...Never really got this deep in one...Kind of interesting if I wasn't so busy other places! I'll update when I get back there!



   
ReplyQuote