I am probably making this more difficult than it is, but I am trying to add a swipe badge to secure 2 floors on a TAC32. I am getting myself confused on how do I address the input to allow access to floors thru controller so I dont have to engineer circuit to bypass security when in F.S.? I have spare inputs, just not sure how to address it.



   
Quote
(@aquadag)
Estimable Member
Joined: 17 years ago
Posts: 173
 
you don't have to engineer anything on the car side just use an extra set of n/o contacts, in parallel to your security system, on the phase 2 sw. to close when you turn phase 2 on, bypassing your security circuit. Simple but effective.

Last edited by aquadag; 07/17/13 03:01 AM.


   
ReplyQuote
(@wpeak)
Estimable Member
Joined: 17 years ago
Posts: 57

   
ReplyQuote
(@aquadag)
Estimable Member
Joined: 17 years ago
Posts: 173
 
you should have a bypass circuit input on the card reader add a set of n/o contacts to your fire service phase 2 keyswitch. put these to your bypass(disable) card reader in put. these should be n/o so that when you turn the key to phase 2 the switch closes and puts the card reader on by pass. which disables the card reader. you will have to buy a new set of keyswitch contacts from a vendor usually.



   
ReplyQuote
(@aquadag)
Estimable Member
Joined: 17 years ago
Posts: 173

   
ReplyQuote
(@john-jay)
Prominent Member
Joined: 17 years ago
Posts: 798
 
another way is to add an ice cube relay with the same coil voltage as the fire service light in the car. just parallel the coil with the fire service light, use the n/o contacts to jump around the security contacts. when the car goes on fire service the relay picks and you enable the car call buttons. simple and easy.



   