330A Question

7 Posts
3 Users
0 Reactions
2,255 Views
(@wltr00)
Honorable Member
Joined: 17 years ago
Posts: 359
Topic starter   [#37823]
Replaced a hall board on the 3rd floor and fixed the problem but the hall board now won’t latch a call. Is there some programming that needs to be done to the replacement board for it to work? Thanks



   
Quote
 MX4
(@mx4)
Estimable Member
Joined: 17 years ago
Posts: 226
 
Make sure you reset the controller after changing the board so it scans for the new node. Sometimes you may need to drain the CAP on cpu. I assume you have it addressed correctly via the S4 switch on board. Check power supply for 24-25vdc. You can also do a pin test for the Lon network at controller to make sure it sees the board in the network.

Now a question for you haha… how the heck did you get a HPBHNA board!!? I can’t find them anywhere



   
ReplyQuote