Elevator Forum

Escape hatch questi...
 
Notifications
Clear all

Escape hatch question

4 Posts
1 Users
0 Reactions
3,807 Views
(@hog451)
Joined: 1 second ago
Posts: 0
Topic starter   [#29387]
Does anyone know the minimum size and clearance requirements for an escape hatch?

Last edited by hog451; 06/04/20 09:21 PM.


   
Quote
(@hog451)
Joined: 1 second ago
Posts: 0
Topic starter  
I found the minimum size it's 400 mm or roughly 15 3/4". How do you define free and clear? Is 28" acceptable?



   
ReplyQuote
(@john jay)
Joined: 1 second ago
Posts: 0
 
A17.1-2016-2.14.1.5.1, states that for a passenger elevator. The exit shall be able to allow the unobstructed passage of a pipe measuring, 12"x20"x59" at an angle of not less than 60 degrees from horizontal. There needs to be clearance 42" above the opening. That is what the code reads. Leave it to an engineer to come up with something like this.



   
ReplyQuote
(@hog451)
Joined: 1 second ago
Posts: 0
Topic starter  
I'll put up some white and red tape then.



   
ReplyQuote