Miprom 2SL-1.... FSP Relay?

3 Posts
1 Users
0 Reactions
2,542 Views
 Goat
(@Goat)
Joined: 1 second ago
Posts: 0
Topic starter   [#21158]
Can someone please inform me what the FSP relay is? Top right DPDT ice cube.

Floor Static Position? Dealing with the magnetic dump switches? MAYBY?

Last edited by Goat; 07/17/17 09:59 PM.


   
Quote
(@john jay)
Joined: 1 second ago
Posts: 0
 
Final Slowdown Pilot is an input. Controlled contact of the FSP Relay. Through the MUS and MDS units.



   
ReplyQuote
 Goat
(@Goat)
Joined: 1 second ago
Posts: 0
Topic starter  
Thank you John Jay. That makes perfect sense. Was having an issue with hitting intermediate floors in up direction. FSP was staying high during run. Found bad MUS. Replaced sensor and car runs great.