The owner of the building tell me sometime between 30 min.and 2hours after the elevator parks at 1st floor it went up to the 2nd ans is stuck there. Cd, Lu, F1, Ohs, S relays pulsing. He check the door and now is closed. Johnny I already place the cap between 24d and Pc.Thanks.



   
ReplyQuote
(@cucuvator)
Estimable Member
Joined: 17 years ago
Posts: 81
Topic starter  
Ok guys I find the problem , zener diode of call 2U when gets hot trigger that call and the elevator stuck there.Thank you very much to the people who helped me out there! Thank you all.



   
ReplyQuote
(@garmin)
Eminent Member
Joined: 17 years ago
Posts: 12
 
Measure the voltage between PC and 24D. It should be close to 24 VDC. If 21 or below add capacitor to PC-24D to stabilize voltage and cards will work properly.



   