09/06/2014 11:26 am
When I said every time the door wouldn't close, I meant every time that wasn't caused by a discernible problem.
Topic starter
10/06/2014 8:04 am
The owner of the building tell me sometime between 30 min.and 2hours after the elevator parks at 1st floor it went up to the 2nd ans is stuck there. Cd, Lu, F1, Ohs, S relays pulsing. He check the door and now is closed. Johnny I already place the cap between 24d and Pc.Thanks.
Topic starter
11/06/2014 9:07 am
Ok guys I find the problem , zener diode of call 2U when gets hot trigger that call and the elevator stuck there.Thank you very much to the people who helped me out there! Thank you all.
28/06/2014 9:06 pm
Measure the voltage between PC and 24D. It should be close to 24 VDC. If 21 or below add capacitor to PC-24D to stabilize voltage and cards will work properly.
12/08/2014 12:54 am
maybe i have prints send your mail
22/08/2014 10:39 am
sounds like vicosity control.
valve needs to be sized
valve needs to be sized