Hi everyone,fault 11 every morning,Relay pilot leds F1,F2,F8.
I got the fault code manual but missing the Dc drive page.

Thanks



   
Quote
(@john jay)
Joined: 1 second ago
Posts: 0
 
This fault indicates a field loss. I would start with checking for loose connections in the Field Circuit.Why you are only getting it in the morning is unusual. Check the field Parameters. Rated Field Current should reflect the Jumper on the Field Feedback Board.



   
ReplyQuote
(@john jay)
Joined: 1 second ago
Posts: 0
 
This fault indicates a field loss. I would start with checking for loose connections in the Field Circuit.Why you are only getting it in the morning is unusual. Check the field Parameters. Rated Field Current should reflect the Jumper on the Field Feedback Board.



   
ReplyQuote
(@NOTIME)
Joined: 1 second ago
Posts: 0
 
im goint to remove the Link try as soons as you can

https://www.dropbox.com/s/khlr68u6jmagglk/Drive%20DC.pdf?dl=0



   
ReplyQuote
(@cucuvator)
Joined: 1 second ago
Posts: 0
Topic starter  
Thanks guys the are loose connections on field board.



   