Elevator Forum

Notifications
Clear all

MIPROM 21

11 Posts
1 Users
0 Reactions
9,481 Views
(@Garmin)
Joined: 1 second ago
Posts: 0
Topic starter   [#4556]
Can anyone help on a miprom 21 problem. Keep getting 41 fault. Car runs but only makes floor to floor runs and throws 41 faults. Already changed encoder and speed boards.



   
Quote
(@Broke_Sheave)
Joined: 1 second ago
Posts: 0
 
Commutation???



   
ReplyQuote
 E311
(@E311)
Joined: 1 second ago
Posts: 0
 
41-saw the intermediate speed (67%) out of tolerance. May be a problem with the tach on the motor or an issue with the ETS board (not uncommon) Make sure your TM switch is correct and or your hoistway slow downs are correct.

Last edited by E311; 09/07/12 09:41 PM.


   
ReplyQuote
(@Garmin)
Joined: 1 second ago
Posts: 0
Topic starter  
A/C drive. No generator



   
ReplyQuote
(@Garmin)
Joined: 1 second ago
Posts: 0
Topic starter  
Replaced ETS and NTS boards. Ran set up and they are in tolerance.



   
ReplyQuote
(@Broke_Sheave)
Joined: 1 second ago
Posts: 0
 
Originally Posted By: Garmin
A/C drive. No generator

Still doing it?

Allen Bradley 1336 digital drive or Baldor 914 analog? (Both are the only AC's I know that are installed on this equipment.

If 1336 No NTS board. Done internally on the motion adapter board.



   
ReplyQuote
 jkh
(@jkh)
Joined: 1 second ago
Posts: 0
 
You may want to check the ets switches in the shaft. Make sure RL2 on the ets board is operating correctly.



   
ReplyQuote
(@Administrator)
Joined: 1 second ago
Posts: 0
 
Is this problem happening consistently or intermittently? This must be an analog AC if you have changed the speed boards. If you have a scope meter you can check your signal coming from the encoder to make sure it's clean back to the drive boards.
Just went through this with a car that had a bad governor shaft causing intermittent encoder faults. Also, check the encoder power supply to make sure it's clean. Good Luck!!



   
ReplyQuote
(@Garmin)
Joined: 1 second ago
Posts: 0
Topic starter  
Its a Baldor 18H drive. RL2 is working properly. It happens on every run.



   
ReplyQuote
 jkh
(@jkh)
Joined: 1 second ago
Posts: 0
 
Garmin how did you make out with this one?



   
ReplyQuote
(@Broke_Sheave)
Joined: 1 second ago
Posts: 0
 
Probably a Baldor 914 originally. Obsolete, so drive was changed to 18H

Originally Posted By: Garmin
Its a Baldor 18H drive. RL2 is working properly. It happens on every run.

Have you checked your motion averages? (And your dictation voltage?)



   
ReplyQuote
Share:
Scroll to Top