Kone Kcm hoistway access

6 Posts
1 Users
0 Reactions
1,432 Views
(@boomer)
Joined: 1 second ago
Posts: 0
Topic starter   [#40652]
We have a Kcm that hoistway access is not working when you key it onto access in the car it throws a 65 error and immediately closes the car door. Tried a new adon board and it does the same thing. Verified key switch wiring to the car too board and menu 4-1 says it’s on inspection but it will not run on access. Anyone ever experienced anything like this?
Thanks



   
Quote
(@Bowtiedrooster16)
Joined: 1 second ago
Posts: 0
 
Did you check and or change the HAS board for that landing? If so did you do a lon download?



   
ReplyQuote
 MX4
(@MX4)
Joined: 1 second ago
Posts: 0
 
K442 Relay is de-energized for car to be on Inspection mode.

Controlling the K442 Relay is by switches on the ground side of the circuit.

K442:1 Relay is energized for car to be on Hoistway Access.



   
ReplyQuote
(@lowoil)
Joined: 1 second ago
Posts: 0
 
Have you checked 7-70 your top floor access #?. I had this change to 0 b4 by itself and an inspector came out and wrote it up. Wouldn't work.



   
ReplyQuote
(@boomer)
Joined: 1 second ago
Posts: 0
Topic starter  
K442 is de-energizing and K442:1 is energized after keying the in car hoistway access switch. As soon as we do that the car is getting a 65 error and the car door powers closed. I’m thinking the LCE is not getting the signal from the adon card? Might try a new ribbon cable if I can get back over there today. 7-70 is set correctly and the route mechanic did try new has boards and performed the Lon download. 5-7-1



   
ReplyQuote
(@john jay)
Joined: 1 second ago
Posts: 0
 
The elevator thinks it is on cartop inspection, or MR inspection. Could be a wiring mistake. You may want to meter the inspection circuit with the wiring diagram.



   
ReplyQuote