Elevator Forum

Notifications
Clear all

gal movfr

6 Posts
1 Users
0 Reactions
11.6 K Views
(@Vatorgator)
Joined: 1 second ago
Posts: 0
Topic starter   [#14506]
mechanic indicates he is getting a frequency failure when the doors start to close, which initiates a reopen. if he makes close speed faster, it does not happen, any ideas.



   
Quote
 jkh
(@jkh)
Joined: 1 second ago
Posts: 0
 
What is your parameter "0" set at? (It should be 30hz)



   
ReplyQuote
(@uppo72)
Joined: 1 second ago
Posts: 0
 
That's weird. You would think that if the VF is failing it would be at all freq's. What about the basics, ie close signal, door scanner signal etc?



   
ReplyQuote
(@Vatorgator)
Joined: 1 second ago
Posts: 0
Topic starter  
easy mistake to make, mistakenly adjusting parameter 0, which is Max speed close, not Hi speed close. so if you adjust parameter 0 below the value set in Hi speed close parameter 4, then when the doors start to close you get frequency failure, and the reopen relay will turn on, if you have wiring to the reopen circuit, which typically goes to your photo eye wiring, the doors will reopen. set parameter 0 back to 30, and then adjust hsc for correct speed, and all is well.
thanks JKH



   
ReplyQuote
(@traction)
Joined: 1 second ago
Posts: 0
 
Does anyone know what causes parameter checksum error with these operators? I had a new one that wasn't working right and was generating this fault, I changed a the board and all was good.



   
ReplyQuote
 jkh
(@jkh)
Joined: 1 second ago
Posts: 0
 
I've never seen the "checksum" error.



   
ReplyQuote