Elevator system anatomy: what every part does and which ones fail

An elevator is not a single machine; it is a collection of subsystems that each have one job. When a car stops between floors, the fastest diagnosis comes from knowing which subsystem could physically produce that symptom – not from starting at the controller and working outward.

The parts, in power order

Subsystem Job Typical failure you will see
Traction machine Moves the car and counterweight by driving the sheave Noise under load, brake drag, gearbox oil loss, encoder drift
Ropes / belts Couple car and counterweight to the sheave Uneven wear, broken wires, tension imbalance, belt rib damage
Counterweight Balances roughly the car plus 40-50% of rated load Guide shoe wear, tie-rod slack, weight stack movement
Car frame and platform Carries the load to the sling and safeties Loose sling bolts, platform deflection, isolation pads
Guide rails and shoes Constrain travel in both axes Roller flat spots, rail joint misalignment, oil starvation
Governor and safeties Detect overspeed and grip the rails Sticking safety, dry governor rope, wrong pull-through tension
Buffers Arrest the car or counterweight at the pit Oil loss, oil contamination, switch not resetting
Doors and interlocks Control access and prove the hoistway is closed The single largest source of callbacks: alignment, gibs, closed switches, operator cams
Controller Sequences motion, speed and levelling Mostly reports faults caused by other subsystems

Why “it stopped between floors” is usually not a controller fault

A controller stops the car deliberately when a safety input opens. The productive question is not “what did the controller do” but “which input opened, and why”. Most between-floor stops trace to one of four families:

  • Door circuit — an interlock or closed switch dropped out in motion, often a worn contact rather than a mis-adjusted door.
  • Safety chain — pit switch, governor switch, or a slack-rope device operated.
  • Drive fault — overcurrent, position loss, or encoder feedback error.
  • Power — a phase loss or voltage sag that the controller recorded as a fault.

Traction versus hydraulic: the split that changes everything

If the building has a hydraulic unit, add the following to the list before touching the controller: oil level and temperature, jack seal condition, valve behaviour, and the pump/motor coupling. Hydraulic faults are frequently thermal – the car is fine cold and drifts or sinks when the oil is hot, which is a valve or seal problem, not a control problem.

Field habit worth keeping: when a unit stops unexpectedly, photograph the controller fault list before clearing anything, note the load in the car and its position in travel, then check the fault against the mechanical history of that unit. Fault codes without context lead to repeat calls.

Where to read more

Component-level questions are covered in the library entries on control systems, door systems, and the safety chain. If you are chasing a live fault on a specific unit, the forum has threads on most major controllers – start with controller fault.